Installation Method
Exhibit 110.3 illustrates the following correct method of connection:
1. The freshly stripped end of the wire is wrapped two-thirds to three-quarters of the distance around the wire-binding screw post, as shown in Step A of Exhibit 110.3. The loop is made so that rotation of the screw during tightening will tend to wrap the wire around the post rather than unwrap it.
2. The screw is tightened until the wire is snugly in contact with the underside of the screw head and with the contact plate on the wiring device, as shown in Step B of Exhibit 110.3.
3. The screw is tightened an additional half-turn, thereby providing a firm connection, as shown in Step C of Exhibit 110.3. If a torque screwdriver is used, the screw is tightened to 12 lb-in.
4. The wires should be positioned behind the wiring device to decrease the likelihood of the terminal screws loosening when the device is positioned into the outlet box.
