I changed out a residential 3 phase meter base and 150 amp panel to a new 200 amp meter base and 200 amp panel. The 3 phase is used for the A/C condenser and that is all. The set up is the service mast comes through the roof and lands in the meter base. Then a 2" offset nipple joins it to a 4" X 2' junction box. From the junction box a 1" nipple feeds a 3 phase disco that is for the A/C cond. Next out of the bottom of the j-box a 2" LB supplys power to the new 200 amp panel. The inspector wrote that I have it bonded/grounded wrong and I would like to know how I should bond everything? I cant reach the inspector to ask him so here I am. I bonded the grounds and neutrals in the 200 amp panel and landed my ground rod and CWG wires there as well. I then ran a #10 ground wire from the 200 amp panel up to the 3 phase A/C disco. Should I have run a #4 wire from the 200 amp panel to a lug in the 4" X 2' junction box as well? The jbox contains the service conductors that are tapped with #6 wire to feed the 3 phase / 30 amp disco. Do I need a 2" bonding bushing on the 2" offset nipple between the meter base and j-box and also a 2" bonding bushing on the 2" LB? Thanks for any help.