I have been asked to assist with an issue related to ground resistance testing for a series of small buildings in close proximity to one another. They have been in service for decades, and as-built drawings are not available. It is “believed” that there are two large ground loops, one surrounding half the buildings and the other surrounding the remaining half. Each building has some type of lightning protection system (I have not yet visited the site, so my knowledge is limited). Because of the types of materials stored in the buildings, they are required to undergo a periodic certification process. The process requires confirmation of the resistance of the grounding electrode system. I am told that this cannot be confirmed, and therefore there is an outstanding deficiency in the certification reports. That is because the 3-point fall-of-potential test requires placing probes outside the sphere of influence of the grounding electrode system, and the ground loops are too big.
Two Questions:
1. Is there a viable method of precisely locating the two large ground loops? I don’t think walking around the campus with a metal detector is likely to succeed. Is there a way to impose a signal onto the loop, starting at one of the buildings, and detecting that signal using some type of detector that you can carry around the campus?
2. To what extent can the presence of a grounding electrode system associated with one building adversely impact the results of a fall-of-potential test being performed on the grounding electrode system associated with a nearby building? It has been suggested that we abandon the existing ground loops in place and install an individual GES at each building.
Two Questions:
1. Is there a viable method of precisely locating the two large ground loops? I don’t think walking around the campus with a metal detector is likely to succeed. Is there a way to impose a signal onto the loop, starting at one of the buildings, and detecting that signal using some type of detector that you can carry around the campus?
2. To what extent can the presence of a grounding electrode system associated with one building adversely impact the results of a fall-of-potential test being performed on the grounding electrode system associated with a nearby building? It has been suggested that we abandon the existing ground loops in place and install an individual GES at each building.