is fall of potential testing practical for outside processing plants, i'm guessing larger than 20 acres.
all of the structures have ground rings and they are all connected
by my understanding of fall of potential testing you should be 8 to 10 times the largest diagonal of the ring away from the ring with your injector
so say a new structure is built inside the existing facility and a new ring installed.
1-if you tie the new ring to the existing stuff and do the fall of potential test don't you need to test outside of the facility? 8 to 10 times further away from entire facilities interconnected rings. your green rod at the ring , injector 8 to 10 x away and measurement probe in the 60% area(multiple spots)
2- even if you leave the new ring unhooked from existing do you know anything by testing outside of only the new ring (the existing is going to influence (lower) the readings right?)
all of the structures have ground rings and they are all connected
by my understanding of fall of potential testing you should be 8 to 10 times the largest diagonal of the ring away from the ring with your injector
so say a new structure is built inside the existing facility and a new ring installed.
1-if you tie the new ring to the existing stuff and do the fall of potential test don't you need to test outside of the facility? 8 to 10 times further away from entire facilities interconnected rings. your green rod at the ring , injector 8 to 10 x away and measurement probe in the 60% area(multiple spots)
2- even if you leave the new ring unhooked from existing do you know anything by testing outside of only the new ring (the existing is going to influence (lower) the readings right?)