I was on a service call today to check a 200 amp MB panel in a residence with a hot main breaker. The renter had shut it off in the morning so it wasn't hot when I showed up. What I found was the 2p 90 amp furnace breaker right below the main had a bad connection and had gotten really hot. Replaced that breaker and the breaker that sat opposite it, and then turned everything back on. I read 75 amps on A & B phase when I took my readings across the main. They read about even at 89 millivolts from line side breaker lug to load side breaker lug. Does this sound about right?
For fun I checked another 2p 30 amp breaker in the panel that seemed to make a very light buzzing sound. It read 18 amps and around 75 millivolts.
These are all molded case Siemens breakers I was testing. Is there a rule of thumb or some kind of chart saying this many amps should equal this many millivolts or less, etc? Anything above this many millivolts at a given current should be replaced? I've read several of Brian John's posts on the subject, I just haven't seen any hard and fast numbers to go by.
Thanks...
For fun I checked another 2p 30 amp breaker in the panel that seemed to make a very light buzzing sound. It read 18 amps and around 75 millivolts.
These are all molded case Siemens breakers I was testing. Is there a rule of thumb or some kind of chart saying this many amps should equal this many millivolts or less, etc? Anything above this many millivolts at a given current should be replaced? I've read several of Brian John's posts on the subject, I just haven't seen any hard and fast numbers to go by.