At the top of a peanut warehousing dome are 4- 115V 1/2 HP fastened in place fans. FLC 9.8 A
A single phase 120/240V panel supplies a multure wire branch circuit to the fans. All the fans have a single receptacle at each fan location. One leg of the split phase system supplies two receptacles or two fans and the other leg of the split phase system supplies the other two receptacles or two fans. So the circuit has two ungrounded conductors and one neutral. All conductors are #12 THHN. The multi wire branch circuit supplies no other loads.
A double pole 20 amp breaker is the circuits OCPD. The fans are thermally protected. The circuit is energized by a double pole motor rated switch.
Can a motor circuit be supplied by a multi wire branch circuit? For the neutral conductor does not have an ampacity as required by 430.24.
Does the total rating of fastened in place utilization equipment have to remain 50% or less of the branch circuit rating as described in 210.23(A) (2)?
A single phase 120/240V panel supplies a multure wire branch circuit to the fans. All the fans have a single receptacle at each fan location. One leg of the split phase system supplies two receptacles or two fans and the other leg of the split phase system supplies the other two receptacles or two fans. So the circuit has two ungrounded conductors and one neutral. All conductors are #12 THHN. The multi wire branch circuit supplies no other loads.
A double pole 20 amp breaker is the circuits OCPD. The fans are thermally protected. The circuit is energized by a double pole motor rated switch.
Can a motor circuit be supplied by a multi wire branch circuit? For the neutral conductor does not have an ampacity as required by 430.24.
Does the total rating of fastened in place utilization equipment have to remain 50% or less of the branch circuit rating as described in 210.23(A) (2)?