W white stallion Member Location El Paso, Texas Sep 28, 2016 #1 What is the operational clearance for a motor disconnect switch on a fan coil unit mounted above a ceiling? Is it 3 ft.?
What is the operational clearance for a motor disconnect switch on a fan coil unit mounted above a ceiling? Is it 3 ft.?
iwire Moderator Staff member Location Massachusetts Sep 28, 2016 #2 Its really one of those times where the code does not address this issue. There is no way to mount a disconnect switch above a suspended ceiling and comply with all the rules in 110.26.
Its really one of those times where the code does not address this issue. There is no way to mount a disconnect switch above a suspended ceiling and comply with all the rules in 110.26.
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Sep 28, 2016 #3 white stallion said: What is the operational clearance for a motor disconnect switch on a fan coil unit mounted above a ceiling? Is it 3 ft.? Click to expand... Code wise or in real life? Code wise would be 3' or 3'6", but in reality 1' most of the time, 2' if you are lucky.
white stallion said: What is the operational clearance for a motor disconnect switch on a fan coil unit mounted above a ceiling? Is it 3 ft.? Click to expand... Code wise or in real life? Code wise would be 3' or 3'6", but in reality 1' most of the time, 2' if you are lucky.