michalspike

Senior Member
I have a 1130cfm fan coil unit and a humidifier next to each other. Fan coil unit takes probably no more then 600 watts, humidifier is a 1 amp. All my units are 120v. Can i put them on a same breaker or i need to run 2 separate lines? Do i need to put them on Arc-Fault protection if they hidden in the closet behind a door?
 
Unless the manufacturer instructions state other wise, 210.23 would allow them on one circuit.
Your profile indicates 2014 Code which seemingly includes closets as areas where AFCI is required.
 
Here is more support


422.12 Central Heating Equipment. Central heating
equipment other than fixed electric space-heating equipment
shall be supplied by an individual branch circuit.
Exception No. 1: Auxiliary equipment, such as a pump,
valve, humidifier, or electrostatic air cleaner directly associated
with the heating equipment, shall be permitted to be
connected to the same branch circuit.
Exception No. 2: Permanently connected air-conditioning
equipment shall be permitted to be connected to the same
branch circuit.
 