I four fans in one circuit which are also fed from emergency generator in bio lab. Each fan draws full load amps of 3A. Manufacturer has not provided MOCP so engineer shows it calculated as follows:

(1.25x3) + 3 + 3 + 3 = 12.75A.


The breaker size he provided is 20A with #12awg conductors.


However i think the engineer above calculated MCA not MOCP.

According to me calculation should be for MOCP

(2.25x3) + 3 + 3+3 = 15.75A

But above 15.75A is MOCP (maximum overcurrent protection)

So the question I have is should not the breaker be sized 15A and not 20A?
 
I four fans in one circuit which are also fed from emergency generator in bio lab. Each fan draws full load amps of 3A. Manufacturer has not provided MOCP so engineer shows it calculated as follows:

(1.25x3) + 3 + 3 + 3 = 12.75A.


The breaker size he provided is 20A with #12awg conductors.


However i think the engineer above calculated MCA not MOCP.

According to me calculation should be for MOCP

(2.25x3) + 3 + 3+3 = 15.75A

But above 15.75A is MOCP (maximum overcurrent protection)

So the question I have is should not the breaker be sized 15A and not 20A?
If it is a design engineer, they are not designing MOCP, they are calculating circuit ampacity. Manufacturer assigns MOCP.
Refer to don_resqcapt19's post for a valuable reference.
 