Most people think of the NFPA 70E as some sort of guide to working on energized equipment when actually it is just the opposite. There are very rare occasions when energized work is permitted.
Zog's note: If you dont know what "Infeasible" means, look it up; it means "incapable of being done". Dont confuse feasible with convenient.
Energized parts that operate at less than 50 volts to ground are not required to be deenergized if there will be no increased exposure to electrical burns or to explosion due to electric arcs.
Zog's note: Notice that "removal of illumination for an area" was removed by NFPA in the latest printing due to the fact that temporary lighting can be used.
I corrected spelling, and added quote brackets to clearly indicate when 70E text was being quoted. -George
NFPA 70E Article 130.1 Justification for work. Live parts to which an employee might be exposed shall be put into an electrically safe work condition before an employee works on or near them, unless the employer can demonstrate that deenergizing introduces additional or increased hazards or is infeasible due to equipment design or operational limitations.
Zog's note: If you dont know what "Infeasible" means, look it up; it means "incapable of being done". Dont confuse feasible with convenient.
Energized parts that operate at less than 50 volts to ground are not required to be deenergized if there will be no increased exposure to electrical burns or to explosion due to electric arcs.
NOTE 1: Examples of increased or additional hazards include, but are not limited to, interruption of life support equipment, deactivation of emergency alarm systems, shutdown of hazardous location ventilation equipment
Zog's note: Notice that "removal of illumination for an area" was removed by NFPA in the latest printing due to the fact that temporary lighting can be used.
NOTE 2: Examples of work that may be performed on or near exposed energized electrical conductors or circuit parts because of infeasibility due to equipment design or operational limitations include performing diagnostics and testing (e.g., start-up or troubleshooting) of electric circuits that can only be performed with the circuit energized and work on circuits that form an integral part of a continuous process that would otherwise need to be completely shut down in order to permit work on one circuit or piece of equipment.
I corrected spelling, and added quote brackets to clearly indicate when 70E text was being quoted. -George