We use Figure 514.3(B) in the 2014 NFPA 70.

We don't put E-Stops in the circuit. We do use Switched Neutral breakers and seal offs as required per 501.15.

Most of the Farm type fuel pumps I have worked with will not require a seal at the dispenser itself. That is a junction box with the adjacent switch enclosed in a factory sealed chamber. You will need one at the boundary as your raceway leaves the classified area.
 