Background:
-We do work on a farm that actually has 4- 400 amp meters (utility here uses Ronk brand, site isolating device, meters) spread throughout a fairly large farmstead.
-There are a number of typical buildings related to cattle, cold storage buildings related to storing equipment, grain bins with fans, utility buildings, and a dwelling unit, each building, bin site, etc., has a panel set up as a service fed from one of the Ronk's.
Objective:
- they want a generator sized appropriately to feed 2 of the Ronk meter loads (the Ronk's are set up for an auxillary power input, i.e.-manual transfer switch supplied by the Utility), he's already been talking to a supplier about a generator in the 110-125 kw range.
-the farmer might want everything to be automatic (we're thinking 2 ATS's sized for the 2 Ronk meter's loads)
-Instead, we're trying to talk him into setting it up to use the Manual Transfer Switch's that are already in place, we would only have to trench from the generator to each meter box, he could select the loads he needs to operate under the conditions and it would allow him to use a smaller generator.
-He likes the idea of it being automatic, he's not sure employee's will be able to manually operate the system.
Issue:
-we need to do a load calc for the loads he wants to be able to operate off the generator if using an ATS system (2 of the 400 amp Ronk meters).
-I spent half the day at the farm yesterday, the other half in the office working on the load calculation
-I'm having a hard time understanding how to use Table220.102
Our largest load is about 12 grain bin fan motors, in the 5 to 7.5 hp range. Normally, multiple motor loads would be sized at 125% of largest, then 100% remaining motor loads. This table gives you directions to choose the largest of three calculations, one of which is "100% of all loads expected to operate simultaneously". This would be our fan motors as the largest that the Table requires us to use, it doesn't say anything about 125% of largest, then 100% of remaining.
Am I understanding this correctly?
Once I get this part understood, I need to figure out how to blend this load situation into the next table, T220.103, as to the largest load @ 100%, 2nd lardest @ 75%, etc.
Any input from those experienced with using these 2 tables would be appreciated.
thanks,
Sky
-We do work on a farm that actually has 4- 400 amp meters (utility here uses Ronk brand, site isolating device, meters) spread throughout a fairly large farmstead.
-There are a number of typical buildings related to cattle, cold storage buildings related to storing equipment, grain bins with fans, utility buildings, and a dwelling unit, each building, bin site, etc., has a panel set up as a service fed from one of the Ronk's.
Objective:
- they want a generator sized appropriately to feed 2 of the Ronk meter loads (the Ronk's are set up for an auxillary power input, i.e.-manual transfer switch supplied by the Utility), he's already been talking to a supplier about a generator in the 110-125 kw range.
-the farmer might want everything to be automatic (we're thinking 2 ATS's sized for the 2 Ronk meter's loads)
-Instead, we're trying to talk him into setting it up to use the Manual Transfer Switch's that are already in place, we would only have to trench from the generator to each meter box, he could select the loads he needs to operate under the conditions and it would allow him to use a smaller generator.
-He likes the idea of it being automatic, he's not sure employee's will be able to manually operate the system.
Issue:
-we need to do a load calc for the loads he wants to be able to operate off the generator if using an ATS system (2 of the 400 amp Ronk meters).
-I spent half the day at the farm yesterday, the other half in the office working on the load calculation
-I'm having a hard time understanding how to use Table220.102
Our largest load is about 12 grain bin fan motors, in the 5 to 7.5 hp range. Normally, multiple motor loads would be sized at 125% of largest, then 100% remaining motor loads. This table gives you directions to choose the largest of three calculations, one of which is "100% of all loads expected to operate simultaneously". This would be our fan motors as the largest that the Table requires us to use, it doesn't say anything about 125% of largest, then 100% of remaining.
Am I understanding this correctly?
Once I get this part understood, I need to figure out how to blend this load situation into the next table, T220.103, as to the largest load @ 100%, 2nd lardest @ 75%, etc.
Any input from those experienced with using these 2 tables would be appreciated.
thanks,
Sky