I am in the pencil and paper stage of redesigning a farm service and feeder distribution system for expansion and conversion to underground distribution.
There are 2 main large agricultural buildings, a large outdoor processing area and plans for 3 more buildings.
one of the buildings has a load over 200A and will be getting a 300A feeder.
The local utility only has single phase in this rural area.
I am thinking of putting a 800A rated Main lug (Siemens P3 or P4 not sure which yet) panelboard connected to a 800A CT can and using the breakers in the panelboard as the Mains to save on the main breaker.
I have worked on many older services that are just bussbar or gutters off a CT can full of old taps to main breakers and they get kinda squirrely.
I figure the upfront cost on a panelboard will be offset by ease of maintenance and changes that happen regularly.
But now I am wondering if its more standard practice to just have a 800A main?
I'll have a 300, 200, 200 and a 125 or 150 as mains. The 125 or 150 will supply a underground outdoor feeder that will have several hoop houses and small structures 'tapped' off it with GEC and one main breaker at each structure.
What do you all think of using a P3 main lug and having 4 or 5 breakers in it as mains?
The only issue I can think of is the panelboard would not be designed to be limited to 6 mains.
But there was never a limit on those old service gutters full of taps either.
Thoughts?
Thanks in advance.
There are 2 main large agricultural buildings, a large outdoor processing area and plans for 3 more buildings.
one of the buildings has a load over 200A and will be getting a 300A feeder.
The local utility only has single phase in this rural area.
I am thinking of putting a 800A rated Main lug (Siemens P3 or P4 not sure which yet) panelboard connected to a 800A CT can and using the breakers in the panelboard as the Mains to save on the main breaker.
I have worked on many older services that are just bussbar or gutters off a CT can full of old taps to main breakers and they get kinda squirrely.
I figure the upfront cost on a panelboard will be offset by ease of maintenance and changes that happen regularly.
But now I am wondering if its more standard practice to just have a 800A main?
I'll have a 300, 200, 200 and a 125 or 150 as mains. The 125 or 150 will supply a underground outdoor feeder that will have several hoop houses and small structures 'tapped' off it with GEC and one main breaker at each structure.
What do you all think of using a P3 main lug and having 4 or 5 breakers in it as mains?
The only issue I can think of is the panelboard would not be designed to be limited to 6 mains.
But there was never a limit on those old service gutters full of taps either.
Thoughts?
Thanks in advance.