Hi folks,
I would like to verify a few things here before I quote a job. Customer lives on a farm. There is a yard pole with 200A breaker on the pole. Drop wires connect to wires at a weatherhead, down conduit to meter can, then 200A circuit breaker can, then back up in 2nd conduit out of top of breaker can, to weather head and attach to insulator rack to go to the various building, including the house.
That is the existing installation. The customer wants to upgrade the panelboard in the home with a 200A panelboard. It is aerial now, with three uninsulated conductors, and I'm going to change that out to 1/0 ns1 triplex with XLPE insulation (205A rating). Of course, new SE cable down to a new 200A breaker mounted on corner of house, then SER through crawl space to panelboard in basement. There is at present no ground rod at the yard pole, or at the house.
Here's the question:
I would like to run the GEC from the neutral at the top of the pole straight down the pole to the ground rods rather than come out of the meter can. I understand that this provides better lightning protection than bringing the GEC out of the lug in the meter can.
I'm also wondering if I should do the same at the house end of the triplex, ie. connect to the neutral before the weatherhead and run the GEC down the side of the house to the ground rods.
Opinions? Does this really make for a better installation as far as lightning/transient protection? Or should I just run the GEC out of the bottom of the meter can at the pole and the main breaker at the house?
Thanks for the help.
Flick
[ January 09, 2006, 11:02 PM: Message edited by: flick ]
I would like to verify a few things here before I quote a job. Customer lives on a farm. There is a yard pole with 200A breaker on the pole. Drop wires connect to wires at a weatherhead, down conduit to meter can, then 200A circuit breaker can, then back up in 2nd conduit out of top of breaker can, to weather head and attach to insulator rack to go to the various building, including the house.
That is the existing installation. The customer wants to upgrade the panelboard in the home with a 200A panelboard. It is aerial now, with three uninsulated conductors, and I'm going to change that out to 1/0 ns1 triplex with XLPE insulation (205A rating). Of course, new SE cable down to a new 200A breaker mounted on corner of house, then SER through crawl space to panelboard in basement. There is at present no ground rod at the yard pole, or at the house.
Here's the question:
I would like to run the GEC from the neutral at the top of the pole straight down the pole to the ground rods rather than come out of the meter can. I understand that this provides better lightning protection than bringing the GEC out of the lug in the meter can.
I'm also wondering if I should do the same at the house end of the triplex, ie. connect to the neutral before the weatherhead and run the GEC down the side of the house to the ground rods.
Opinions? Does this really make for a better installation as far as lightning/transient protection? Or should I just run the GEC out of the bottom of the meter can at the pole and the main breaker at the house?
Thanks for the help.
Flick
[ January 09, 2006, 11:02 PM: Message edited by: flick ]