Hi ,
Do you think that I can estimate a remodeled warehouse load supplied by the existing 120/240V, 4wire, 3 phase service
this way ?????????;
General ltg w/ 25% LCL = 2400VA @ 120/240v, 1 ph. = 10A
Gen. use recept @ 100= 2400VA= @ 120/240, 1ph= 10A
special . use recept @ 100= 4800VA= @ 120/240, 1ph= 20A
miscel. @ 100= 1200VA= @ 120/240, 1ph= 5A
Motorized load @ 100= 12,450VA @ 415V, 1ph= 30A (some used the high leg)
roof mtd AC load @ 100= 12,450VA @ 415V, 3ph= 30A
sub total , 2pole+3 ph loads= 60A
sub total, 1 ph, grounded loads= 45A
Largest motor @ 25%= 2075VA @ 415V= 5 A
120% PF for existing-old motorized loads= (13000 x 1.2= 15,600 / 415V= 38A
Concluded that;
minimum service @ 120/240, 3 ph, 4w required is; 148A
Thank you
mbrooke
Batteries Included
United States
Technician
Sounds like EU voltages. Except for the 120V.
Its this:
attachment.php
Delta high leg is great for long runs because standard 208-230 volt motors are unlikely to encounter under voltage issues.
mbrooke
Batteries Included
United States
Technician
mbrooke
Excellent graphics....can I ask what program was used to generate, or was this all cut and paste ?
They are Mike Holt's. Not sure what program he or his team made them on, but they sure are the best graphics bar none.
But no mention of 415V.
Oppps- missed that :ashamed1: But to be fair you do get 415 volts L-N on a 240/480 delta.
Besoeker
UK
Don't see how but then I'm thick according to one of the mods here.
jumper
Yes, but the OP does not have a wye secondary.
A 240V wye would be uncommon for most typical applications because unshown in that graphic is the center point ground connection and one would get 139V for L-N(G), Not very useful for receptacles and such.
And please please no one bring up an ungrounded wye, my little brain cannot handle it.:D