Do you think that I can estimate a remodeled warehouse load supplied by the existing 120/240V, 4wire, 3 phase service
this way ?????????;:?
General ltg w/ 25% LCL = 2400VA @ 120/240v, 1 ph. = 10A
Gen. use recept @ 100= 2400VA= @ 120/240, 1ph= 10A
special . use recept @ 100= 4800VA= @ 120/240, 1ph= 20A
miscel. @ 100= 1200VA= @ 120/240, 1ph= 5A
Motorized load @ 100= 12,450VA @ 415V, 1ph= 30A (some used the high leg)
roof mtd AC load @ 100= 12,450VA @ 415V, 3ph= 30A
sub total , 2pole+3 ph loads= 60A
sub total, 1 ph, grounded loads= 45A
Largest motor @ 25%= 2075VA @ 415V= 5 A
120% PF for existing-old motorized loads= (13000 x 1.2= 15,600 / 415V= 38A
Concluded that;
minimum service @ 120/240, 3 ph, 4w required is; 148A
Thank you