J jap Senior Member Occupation Electrician Oct 29, 2015 #1 16 CCC in 3/4" Emt #12 thhn ,OCPD 15 amp max? JAP>
luckylerado Senior Member Location Lake of the Ozarks Oct 29, 2015 #2 Yes. 50%*30A Incidentally, if you are putting a grounding wire in the 3/4" EMT, you are over on fill. Last edited: Oct 29, 2015
Yes. 50%*30A Incidentally, if you are putting a grounding wire in the 3/4" EMT, you are over on fill.
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Oct 29, 2015 #3 luckylerado said: Indecently. . . . Click to expand... Incidentally? (Sorry, couldn't resist.)
luckylerado Senior Member Location Lake of the Ozarks Oct 29, 2015 #4 charlie b said: Incidentally? (Sorry, couldn't resist.) Click to expand... Thx