I am looking for the fault curent calculation or formula. I know the avalible fault curent at the transformer. however i do not know the impedence or the kva.
Re: Fault Curent calculation
Mike Holt has a great download available on his "free stuff" page that explains the whole proceedure of doing point to point fault current calcs. check out Mike Holts Free Stuff
Normally, you need to know the available current or use teh impedance and kva rating to determine it. If you have been given the avail current to start with, you probably have all you need.
If you find the impedance and kVA to calculate the available kVA, your figures will likely be different than you have been given. We give the maximum possible based on the lowest impedance transformer we have in that size, assuming an infinite bus and a bolted fault. :D
Are you referring to the "Short-Circuit Point-to-Point Calculations Book"?
I tried downloading the "Short-Circuit Calculator" listed on Mike's site, but it wouldn't open in Excel. It's shown as being a Lotus 123 speadsheet.
I sometimes use a fault current calculator program that I downloaded (free) from the Bussman website. It runs just fine on Windows XP. Have you tried that?