I don’t have access to power analysis software, so I’m doing manual point-to-point short circuit calculations and I have questions about the propagation of fault current across transformers. I’m using the formula described below, but I never use formulas that I don’t understand so I wanted to make sure I fully understand this:
In general, for calculation of downstream fault current (I2) from known upstream fault current (I1), the assumption is the line voltage drop is the same in either case, so the relationship exists: I1 * Z1 = I2 * (Z1+Z2), which simplifies to I2 = I1 * 1 / (1 + Z2/Z1). In the above procedure, 1 / (1 + Z2/Z1) corresponds to the M multiplier and Z2/Z1 corresponds to the f-factor, therefore Z2/Z1 = (I1 * V1 * 1.732 * %Z) / (100,000 * KVA). Z2 in this case is the impedance of the primary winding, which can be calculated from %Z by Z2 = Zabs = %Z/100 * Zbase = %Z/100 * V2 * 1.732 / (1000 * SKVA). Z1 is simply V1/I1. Dividing Z2 by Z1 yields the same formula for the f-factor in the method above. I understand that this method ignores the X/R ratios of the line impedances. My questions:
1. In step C, I1 = Isca(p) and I2 = M * Isca(p). Therefore I2 is the fault current as seen by the primary side of the transformer during a secondary fault, which is then converted to the current on the secondary using the standard transformer conversion formula. Does this mean that I2 would be the value I use to determine clearing time on the primary OCPD for arc flash purposes?
2. Step C does not use any efficiency or power factor for conversion. I can get efficiency and X/R ratios from the transformers here. In fault current situations, are these adjustments typically used?
In general, for calculation of downstream fault current (I2) from known upstream fault current (I1), the assumption is the line voltage drop is the same in either case, so the relationship exists: I1 * Z1 = I2 * (Z1+Z2), which simplifies to I2 = I1 * 1 / (1 + Z2/Z1). In the above procedure, 1 / (1 + Z2/Z1) corresponds to the M multiplier and Z2/Z1 corresponds to the f-factor, therefore Z2/Z1 = (I1 * V1 * 1.732 * %Z) / (100,000 * KVA). Z2 in this case is the impedance of the primary winding, which can be calculated from %Z by Z2 = Zabs = %Z/100 * Zbase = %Z/100 * V2 * 1.732 / (1000 * SKVA). Z1 is simply V1/I1. Dividing Z2 by Z1 yields the same formula for the f-factor in the method above. I understand that this method ignores the X/R ratios of the line impedances. My questions:
1. In step C, I1 = Isca(p) and I2 = M * Isca(p). Therefore I2 is the fault current as seen by the primary side of the transformer during a secondary fault, which is then converted to the current on the secondary using the standard transformer conversion formula. Does this mean that I2 would be the value I use to determine clearing time on the primary OCPD for arc flash purposes?
2. Step C does not use any efficiency or power factor for conversion. I can get efficiency and X/R ratios from the transformers here. In fault current situations, are these adjustments typically used?