Submitted a permit for a 200 amp meter main combination panel replacement today in the city of Titusville Florida. This is the only city that has ever requested a fault current calculation for a service upgrade. If I don’t provide the fault current calculation then I’m told I have to use 22KA rated breakers at the service equipment and indoor panel. This is a small residential neighborhood and the house is a 1700 square-foot home...
highly unlikely the transformer from utility is more than 10 KA.
This request for a fault current calculation would seem reasonable on a commercial building . The building official is requesting that I get A letter from utility identifying the transformer Ampere rating. This seems to be an unreasonable request for a residential application. Correct me if I’m wrong.
Sent from my iPhone using Tapatalk
highly unlikely the transformer from utility is more than 10 KA.
This request for a fault current calculation would seem reasonable on a commercial building . The building official is requesting that I get A letter from utility identifying the transformer Ampere rating. This seems to be an unreasonable request for a residential application. Correct me if I’m wrong.