I'm trying to complete some fault current calculations and I need a little assistance.
We have a 150KVA Transformer with a 5.5% Impedance. 13.8KV Primary to 120/208 Secondary.
We have parallel 400s running to a gutter, where they are tapped to feed 3 disconnects and a house panel. Wire size to the disconnects are 300MCM, 3/0, 3/0, and #6.
When calculating the fault current, do I treat each disconnecting means as a separate system, or should I treat the entire system as one? Is the fault current limited by the lowest calculated section of the system? This is the first time I've ever had to do one of these, as normally all of these things are included in the engineered plans for the installation. Any help or insight would be greatly appreciated!
We have a 150KVA Transformer with a 5.5% Impedance. 13.8KV Primary to 120/208 Secondary.
We have parallel 400s running to a gutter, where they are tapped to feed 3 disconnects and a house panel. Wire size to the disconnects are 300MCM, 3/0, 3/0, and #6.
When calculating the fault current, do I treat each disconnecting means as a separate system, or should I treat the entire system as one? Is the fault current limited by the lowest calculated section of the system? This is the first time I've ever had to do one of these, as normally all of these things are included in the engineered plans for the installation. Any help or insight would be greatly appreciated!