I'm familiar with calculating KAIC from the fault current calculation spreadsheet available on this website. However, I'm surprised to notice no intake for the voltage on the primary side of the transformer. I know this is geared toward applications where this would be medium voltage and utility service transformers, anywhere from 10 kV thru 25 kV.
What is the strategy for calculating how KAIC is affected by customer-owned, utilization voltage-to-utilization voltage transformers? Such as a 480V primary and a 208V secondary. Or other combinations? Does frequency play a role? I often have applications at 50 Hz.
Given KAIC on the primary, and the voltages of the transformer, the KVA, and the percent impedance, how does one calculate KAIC on the secondary?
Example:
225 kVA
2.5% impedance
480V primary
208V secondary
Fault current available at the primary is 20 KA.
What KAIC do I need on the secondary equipment?