R rdrigg Member Feb 28, 2008 #1 When determining "C" values of conductors how is that changed when you use conductors in parallel?
charlie b Moderator Staff member Location Lockport, IL Occupation Retired Electrical Engineer Feb 28, 2008 #2 Sorry, but I don't know what you mean by "C values."
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Feb 28, 2008 #3 Look at page two of this document.
zog Senior Member Location Charlotte, NC Feb 28, 2008 #4 For parallel runs, multiply C values by the number of conductors per phase.
J jghrist Senior Member Feb 28, 2008 #5 zog said: For parallel runs, multiply C values by the number of conductors per phase. Click to expand... Which is done by the factor "n" in the Bussman equation. n = Number of conductors per phase (adjusts C value for parallel runs) Click to expand...
zog Senior Member Location Charlotte, NC Feb 28, 2008 #7 Oops, you are right, guess I should have looked at that link. The "n" isnt in any other of my references for the point to point method, guess Busmann added that in there.
D davidr43229 Senior Member Location Columbus, Oh Feb 29, 2008 #8 The C value is a conservative value, instead of using the X / R ratio. Be careful when determining if you have magnetic or non magnetic conduits. http://www.cooperbussmann.com/7/FreeSoftware.html#Short-Circuit Current Calculator Just my $.02
