My POCO supplies me with their information for faults at the transformer. They send it as: 5100 amps L-N, 240v. In this case 120/240 single phase.
Mike Holts fine calculator does not like L-N. A spreadsheet I made 20 some years ago calculates the L-N faults as 1.5 times the L-L fault. Note 2 on page 7 of MH's Short Circuit Calculations Book indicates this is correct even though his spreadsheet never displays that answer for L-N faults.
Should I use 5100/1.5=3400 as my input for MHs calculator?
Mike Holts fine calculator does not like L-N. A spreadsheet I made 20 some years ago calculates the L-N faults as 1.5 times the L-L fault. Note 2 on page 7 of MH's Short Circuit Calculations Book indicates this is correct even though his spreadsheet never displays that answer for L-N faults.
Should I use 5100/1.5=3400 as my input for MHs calculator?