I agree with don_resqcapt19, of course. There are some limitations as system impedance and may be, connected cables-at 480 V and/or at 208 V.
In IEEE 141/1993 IEEE Recommended Practice for Electric Power Distribution for Industrial Plants ch.4 Short-circuit current calculation sub.4.3.2 Type of short-circuit it is stated:
"In calculating the maximum short-circuit current, it is assumed that the short-circuit connection has zero impedance (is "bolted") with no current-limiting effect due to short-circuit itself. It should be recognized, however, that actual short-circuits often involve arcing, and variable arc impedance can reduce low-voltage short-circuit current magnitude appreciably.
In low-voltage systems, the minimum values of short-circuit current are sometimes calculated from known effects of arcing. Analytical studies indicate that the sustained arcing short-circuit currents, in per unit of bolted fault values, may be typically as low as:
a) 0.89 at 480 V and 0.12 at 208 for three-phase arcing."