Re: Fault Current Rating
FAULT CURRENT: If you would take a metal bar and short out the Secondary of a transformer that would feed a sub-station, that would be the available Maximum fault current at that location.
As you proceed down-stream from the sub-station with wiring, you will have resistance in the system and the "FAULT CURRENT" will be less due to the resistance of the wiring.
For Example: On a fuse that has a rating of 15, 30, 100 Amperes, etc. there will be a AIC rating of 250 K Amps shown on the barrel of the fuse, or 300 K Amps. This rating will keep the fuse from blowing apart when a fault to ground happens on your system. Many years ago we would experience fuses that would blow apart, because they were not rated for the Fault-Current like they are today.
The same with your Circuit-Breakers in your Panel Board. If you do not see a Fault rating the Circuit Breaker is rated for 5000 Amps Interrupting rating, (AIC). Above that you will see the CB rating of 10K AIC.
At our Industry Site, we have a documented Fault Current of 50,000 AIC, and as we continue downstream with wiring and equipment the AIC will be Lower, and we have this documented on a print.