I would appreciate if you could point out any errors in the following reasoning.
2500 kVA transformer, 12.47kV primary, 480Y/277V secondary, 5.75% Z.
Using the infinite primary bus method, I get fault current of 52296A at secondary terminals (bolted 3 phase fault).
(2500 kVA / (480V * 1.732)) / 0.0575 = 52296A
MVA method:
Transformer admittance: 2.5 MVA / 0.0575 = 43.47 MVA
43.47 MVA / (480 * 1.732) = 52288 A (due to rounding errors)
The utility engineer supplied the following data for the 12.47 kV power lines coming into the plant:
When I do the calculation with the 1552 A value, this is what I get, using the MVA method:
Utility fault current MVA: 12.47 kV * 1.552 kA = 19.35 MVA
Transformer admittance: 2.5 MVA / 0.0575 = 43.47 MVA
Series combination: 1 / ( 1/19.35 + 1/43.47 ) = 13.39 MVA fault at transformer secondary
Convert to amps: 13390000 / (480 * 1.732) = 16106 A fault current at transformer secondary
The reason I am asking is that this seems rather low compared to the infinite bus method, and this is my first job doing the calculations, so I just wanted to put it out there to see if it looked reasonable. Do I need to use the X/R somewhere? This is in a small town, so it is not right along a main transmission line.
thank you
2500 kVA transformer, 12.47kV primary, 480Y/277V secondary, 5.75% Z.
Using the infinite primary bus method, I get fault current of 52296A at secondary terminals (bolted 3 phase fault).
(2500 kVA / (480V * 1.732)) / 0.0575 = 52296A
MVA method:
Transformer admittance: 2.5 MVA / 0.0575 = 43.47 MVA
43.47 MVA / (480 * 1.732) = 52288 A (due to rounding errors)
The utility engineer supplied the following data for the 12.47 kV power lines coming into the plant:
3-Phase FAULT CURRENT: | 1552 A |
Line-Line FAULT CURRENT: | 1344 A |
1-Phase FAULT CURRENT: | 1727 A |
System X/R: | 4.11 |
Line to Line Voltage (kV): | 12.47 |
When I do the calculation with the 1552 A value, this is what I get, using the MVA method:
Utility fault current MVA: 12.47 kV * 1.552 kA = 19.35 MVA
Transformer admittance: 2.5 MVA / 0.0575 = 43.47 MVA
Series combination: 1 / ( 1/19.35 + 1/43.47 ) = 13.39 MVA fault at transformer secondary
Convert to amps: 13390000 / (480 * 1.732) = 16106 A fault current at transformer secondary
The reason I am asking is that this seems rather low compared to the infinite bus method, and this is my first job doing the calculations, so I just wanted to put it out there to see if it looked reasonable. Do I need to use the X/R somewhere? This is in a small town, so it is not right along a main transmission line.
thank you