Fault Current
gregoryfast
Alaska
I am putting together an Excel spreadsheet of transformers in our system. I wanted to come up with a formula to automatically calculate the fault current from the name plate data. Does anyone have a simple way of doing this?
If it can be to the nearest 1000 amps, that would be OK.....
I have seen a website (oberon) that has a calculator when you enter the name plate data. It does it for you. But it would take a long time for me to enter each transformer separately.
Also, is there a standard distance for giving the value of the fault current?
Re: Fault Current
Calculation is required at the line terminals of the equipment.
I have never witnessed damage to equipment, from a fault, other at the location of the fault.
Don't tell me that the AIC rating of equipment is forever. What is the big deal with fault current calculations?
There is a lot of equipment breaking down and degrading. It's a fact of life and a law of physics.
Re: Fault Current
If you are interested in an estimate of the fault currrent assuming an infinite fault capacity the following will do the job
% R, %X and %Z are name plate info
Trans X(ohms)=(10)(%X)(Sec volt KV)?/Trans KVA
Trans R(ohms)=(10)(%R)(Sec volt KV)?/Trans KVA
ZTotal = Sq Root(R? + X?)
Isc = Sec Line Voltage/(Zt x 1.73)
If you goto Mike Holts Home Page and look under free stuff there is a fault caculator you can download.
[ July 17, 2003, 12:07 AM: Message edited by: bob ]
Re: Fault Current
Also, for infinite primary calcs you can use:
Isc=transVA/V/trans impedance
So for example, a 300kVA transformer with a secondary voltage of 208/120V and an imperdance of 3%, the calc looks like:
Isc=300000/208/1.73/.03=27790A