Carultch
- Massachusetts
When given a fault current, sourced on the line side of a set of fuses, with downstream circuit breakers, can you take any credit for the fuses in terms of reducing the fault current to the downstream circuit breakers?
I know about the "up, over, down" method, which seems intuitive, but I also see a lot of criticism of its validity. Is there any other calculation you can do with the time-current curves and specifications of fuses and breakers to see if there is a reduction in fault current due to using the fuses?
Or is it the case that if it is not a listed series combination for the full fuse KAIC rating, then it is not an approved series combination for ANY fault current larger than the breaker's KAIC capacity?
Example:
Given 27 kA of available fault on the line side of RK5 fuses, what is the minimum KAIC of a breaker would you need on the load side? Neglect distance of conductor runs, and assume no load side fault sources.
Example: