I have an existing service that will be upgraded by the local utility. The existing service is a 400 amp 600 volt 3 phase 3 wire delta system. It is fed from a pad mount transformer that is leaking oil and needs to be replaced. The current standards here are 600/347 volt 3 phase 4 wire. They are going to install a new pole with three transformers and extend my secondary wiring to the top of the pole and install the 4th (neutral) conductor. They are installing 300 KVA and have indicated that the fault currents on the new system will be slightly higher than the existing system. The new fault current will be around 22k amps at the transformer bushings. The main fusible switch has fuses rated at 300k AIR. These fuses don't concern me. My question is how far down the line do I have to be concerned with the available fault current? The distribution for the building comes from molded case circuit breakers. These feed things like lighting transformers and such. There is also an MCC for the compressor equipment but it has all HRC fusing internally. Do I simply need to check the breakers in the distribution panel to make sure there ratings are higher than the available fault current or do I need to look further than that?