Faulty Transformer

Status
Not open for further replies.

RV6

Member
Location
Saint Charles IL
Hello All. We recently moved into a new commercial faculty. We are trying to figure out our high no load power consumption. Our first bill showed a consumption of 3400kWh while we were moving. During the move we did not use any equipment other than computers, lights and AC for a 1500SQFT office.

We did some digging and found that our Delta-Delta 480V to 240V transformer was putting out a lot of heat. We shut off all the loads on the secondary and measured input current on the 480V primary.

Primary input current (No load)
L1 = 8A
L2 = 8.4A
L3 = 11.5A

Is this typical input current for a unloaded 150kVA transformer?

I just did some more detailed measurements with equipment running and it appears the primary input current is unbalanced. However the voltages are close.

Primary input current (Loaded)
L1 = 29.2A
L2 = 11.4A
L3 = 34.5A

Primary phase to phase voltages (Loaded)
L1-L2 = 494V
L2-L3 = 491V
L1-L3 = 491V

Primary phase to neutral voltages (Loaded)
L1 = 284V
L2 = 285V
L3 = 283V

Secondary phase to phase voltages (Loaded)
L1-L2 = 247V
L2-L3 = 244V
L1-L3 = 243V


Secondary phase to neutral voltages (Loaded)
L1 = 122V
L2 = 213V
L3 = 122V

I called the utility out and they claim the power outside of the building is fine. My electrician thinks the utility is sending us unbalanced power causing the transformer to heat up.

Any ideas? Any help would be appreciated.


TRANS.jpg
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
190717-1799 EDT

RV6:

My electrician thinks the utility is sending us unbalanced power causing the transformer to heat up.
I don't think this electrician knows what he is talking about. What would be the definition of unbalanced power? Does he mean unbalanced voltage? You don't have that. Your voltage balance on both primary and secondary is very good. I do think "L2 = 213V" is a typo, and should read 123. Other measurements do not support a reading of 213.

Whether you have neutrals or not you can imagine you do. On the primary this would be 277 V nominal line to neutral.

Each phase can supply 1/3 of the kVA rating. Thus, full load phase current is 50,000/277 = 180 A. A no load line input current of 10 A is peanuts.

If this were a resistive load it would be about 3000 W.

But it is mostly inductive. But suppose it was all power loss, then you have a continuous 10,000 W load or 10 kW.

Over a 30 day period this would be 320*10 = 320 kWH. This is 1/10 the 3400 you indicated was the bill.

Further your transformer is not itself using 320 kWH because much of the noload current is not resistive.

Someone else can give you a realistic estimate of actual losses in the transformer.

.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
190717-1799 EDT

I do think "L2 = 213V" is a typo, and should read 123. Other measurements do not support a reading of 213.

The secondary is a center tapped 240/120V delta. The nominal voltage for L2 would be 208V, so 213 looks okay.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
We did some digging and found that our Delta-Delta 480V to 240V transformer was putting out a lot of heat. We shut off all the loads on the secondary and measured input current on the 480V primary.

There is no way to know that the transformer is putting out too much heat without using a thermometer.
For a transformer, like your, I wold expect that it feel like a space heater.
 

RV6

Member
Location
Saint Charles IL
There is no way to know that the transformer is putting out too much heat without using a thermometer.
For a transformer, like your, I wold expect that it feel like a space heater.

Thanks for the replies!

The core of the transformer measures around 250F no load. Certain parts of the case are uncomfortable to touch.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The core of the transformer measures around 250F no load. Certain parts of the case are uncomfortable to touch.

If you can touch it at all, it is not overheating.
The center, internal areas, of the transformer is rated for 150C over a 40C ambient.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Remember, Watts = Amps x Volts x Power Factor (x1.732 for 3 phase). The current readings are relatively meaningless because the Power Factor on an unloaded transformer is likely very low, maybe even as low as .3 or less. That means that the WATTS, what you are actually billed for, will be low as well.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
190718-1307 EDT

Jaref's ballpark for PF = 0.3 is certainly a good estimating value with no other knowledge available.

I checked PF on two small transformers using a Kill-A-Watt EZ:

1. Stancor P8662 nominal 120 V in, and 24 V at 2 A out (VA out = 48).

No load input at 123 V
--- 0.04 A, 3.3 W, 5.8 VA, 0.59 PF

2. Signal Transformer A41-175-24 nominal 120 V in, and 24 V at 7.3 A out (VA out = 175).

No load input at 123 V
--- 0.23 A, 4.5 W, 28.8 VA, 0.15 PF


Big difference. Transformer design will determine how these values fall out
 

kwired

Electron manager
Location
NE Nebraska
There is no way to know that the transformer is putting out too much heat without using a thermometer.
For a transformer, like your, I wold expect that it feel like a space heater.
No there isn't, but the heat lost comes from true power losses/resistance and not from reactive current. The more reactive current you have however the more current flows through conductors and the more resistance losses you will have.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
190718-1943 EDT

When you measure the real power input to an unloaded transformer, then that power defines the transformer temperature rise over ambient for whatever cooling conditions exist.

This noload power measurement includes all losses from the reactive current I^2*R, and core losses at noload.

.
 

RV6

Member
Location
Saint Charles IL
Thank you all for the help. They sent out another electrician yesterday to do some measurements. The electrician is going to call the transformer manufacture and see what the transformer losses should be. I might have to look into buying or renting a power analyzer.


We are considering going with a smaller transformer or putting a disconnect on the larger transformer and running small transformer for the lights and office.


Meanwhile I will check what the voltage tap is set at on the primary and measure the 480V line voltage during the off hours. Setting it for a higher voltage should reduce the losses.


I will post with what we come up with.

Thanks again for the help.
 

kwired

Electron manager
Location
NE Nebraska
Thank you all for the help. They sent out another electrician yesterday to do some measurements. The electrician is going to call the transformer manufacture and see what the transformer losses should be. I might have to look into buying or renting a power analyzer.


We are considering going with a smaller transformer or putting a disconnect on the larger transformer and running small transformer for the lights and office.


Meanwhile I will check what the voltage tap is set at on the primary and measure the 480V line voltage during the off hours. Setting it for a higher voltage should reduce the losses.


I will post with what we come up with.

Thanks again for the help.
Voltage may drop once you have some significant loads - if you are going to have any.
 

zog

Senior Member
Location
Charlotte, NC
Thank you all for the help. They sent out another electrician yesterday to do some measurements. The electrician is going to call the transformer manufacture and see what the transformer losses should be. I might have to look into buying or renting a power analyzer.


We are considering going with a smaller transformer or putting a disconnect on the larger transformer and running small transformer for the lights and office.


Meanwhile I will check what the voltage tap is set at on the primary and measure the 480V line voltage during the off hours. Setting it for a higher voltage should reduce the losses.


I will post with what we come up with.

Thanks again for the help.

Why don't you just have the transformer tested?
 

zog

Senior Member
Location
Charlotte, NC
7.2.1.1 Transformers, Dry Type, Air-Cooled, Low-Voltage, Small
Page 28
ANSI/NETA MTS-2019
NOTE: This category consists of power transformers with windings rated 600 volts or less and
sizes equal to or less than 167 kVA single-phase or 500 kVA three-phase.

A. Visual and Mechanical Inspection
1. Inspect physical and mechanical condition.
2. Inspect anchorage, alignment, and grounding.
3. Prior to cleaning the unit, perform as-found tests, if required.
4. Clean the unit.
5. Inspect bolted electrical connections for high resistance using one or more of the following
methods:
1. Use a of low-resistance ohmmeter in accordance with Section 7.2.1.1.B.1.
2. Verify tightness of accessible bolted electrical connections by calibrated torquewrench
method in accordance with manufacturer’s published data or Table 100.12.
3. Perform a thermographic survey in accordance with Section 9.
6. Perform as-left tests.
7. Verify that as-left tap connections are as specified.

B. Electrical
1. Perform resistance measurements through bolted connections with a low-resistance
ohmmeter in accordance with Section 7.2.1.1.A.5.1.
2. Perform insulation-resistance tests winding-to-winding and each winding-to-ground. Apply
voltage in accordance with manufacturer’s published data. In the absence of manufacturer’s
published data, use Table 100.5. Calculate the dielectric absorption ratio or polarization
index.
*3. Perform turns-ratio tests at the designated tap position.

C. Test Values – Visual and Mechanical
1. Compare bolted connection resistance values to values of similar connections. Investigate
values which deviate from those of similar bolted connections by more than 50 percent of
the lowest value. (7.2.1.1.A.5.1)
2. Bolt-torque levels should be in accordance with manufacturer’s published data. In the
absence of manufacturer’s published data, use Table 100.12. (7.2.1.1.A.5.2)
3. Results of the thermographic survey shall be in accordance with Section 9. (7.2.1.1.A.5.3)
4. Tap connections are left as found unless otherwise specified. (7.2.1.1.A.7)

D. Test Values – Electrical
1. Compare bolted electrical connection resistances to values of similar connections.
Investigate values which deviate from those of similar bolted connections by more than 50
percent of the lowest value.
2. Minimum insulation-resistance values of transformer insulation should be in accordance
with manufacturer’s published data. In the absence of manufacturer’s published data, use
Table 100.5. Values of insulation resistance less than this table or manufacturer’s
recommendations should be investigated. The dielectric absorption ratio or polarization
index shall be compared to previously obtained results and should not be less than 1.0.
3. Turns-ratio test results should not deviate more than one-half percent from either the
adjacent coils or the calculated ratio.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
190719-1224 EDT

RV6:

Real power going into a load is no greater than the input volt-amperes.

Your unloaded VA to the transformer is small, therefore the noload real power input (heat being dissipated) is low.

If you really had virtually noload on the transformer, then I suggest the power company has a metering problem for the kWH they billed you. That is assuming billing was for 1 month.

Based on your noload current values, ball park 10 A, your noload power input is way below 3*10*480/1.732 = 8.3 kW. This I have said before, and also there are 24*30 = 720 hours in a 30 day month. Thus, your 1 month billing can not be over 8.3*720 = 5976 kWH for no load, and probably should be around 600 to 1000 kWH.

Your bill showed 3400 kWH. One computer on full time might be 100 W or 720*0.1 = 72 kWH, but you had an air conditioner which is a much bigger load.

Looking at your loaded current assume an average of 25 A, a power factor of 0.6, and 12 hours per day, then added load is less than (3*25*480/1.732)*0.6 = 12.5 kW. But this is on 12 hours per day (assumption) so loaded kWH per month is 12.5*360 = 4500 kWH. But some of that is transformer excitation.

Possibly the power company billing is not that bad.

Put a kWH meter on the load side of the transformer and see what a couple days show.

A TED system might be an inexpensive means to make a rough measurement.

.
 

kwired

Electron manager
Location
NE Nebraska
Hello All. We recently moved into a new commercial faculty. We are trying to figure out our high no load power consumption. Our first bill showed a consumption of 3400kWh while we were moving. During the move we did not use any equipment other than computers, lights and AC for a 1500SQFT office.
Between the AC and heat losses in the transformer I could see that might use that much energy. If transformer is inside the conditioned space, that makes the AC need to work that much more to remove the transformer's heat. If there is a lot of open doors while moving that don't help either, especially if pretty warm outside.
 

RV6

Member
Location
Saint Charles IL
Update: The landlord tells me that the electrician contacted GE and was told that our transformer has been revised several times since installation. They claim that their new transformer will only draw 1.5A VS the 8A we are drawing now. The landlord wouldn't tell me if the 8A was normal. However he did say he would split the $3000-4000 cost of installing a new transformer. Does anyone know the contact number for GE technical support? I am still not sure if the transformer is defective or the landlord is trying to get me to chip in for a repair. I have a hard time believing transformer technology has improved 5 fold in 20 years.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I have a hard time believing transformer technology has improved 5 fold in 20 years.
Decades ago, transformers were often designed to be most energy efficient at 80-100% of full load. Most transformers installed in commercial and educational buildings are rarely loaded above 50% and spend maybe a third of their life not even this high. Because of this load profile, over the years the Dept of Energy created and implemented requirements for general purpose transformers to be most efficient at 35% loading.

So yes, unloaded transformers today are more efficient than in years gone past. The amount of improvement varies by manufacturer and transformer size.
 
I have measured no load losses on a bunch of 15 KVA transformers. I have found no load losses to be about 3 times higher in 20 year old units over a unit several years old, 180 watts compared to 60. I had a very old unit, and it drew 300 watts
 