Hello, we have treadmills in our fitness center that's rated for 240v, single phase.
We've been getting complaints of the treadmill motors overheating.
The branch circuit panel is less than 50' away. The tech that services the treadmill says the minimum operating voltage needed is 210v.
Our building supply is 208/120v.
My question: Can the branch circuit panel transformer's primary side Full Capacity Above Normal taps be adjusted to boost secondary voltage?
If so, will this affect transformer operation or trip its feeder circuit breaker should the utility's supply voltage fluctuate?
ie: present voltage @ substation secondary - 500vac, this is normally 480vac.
Hope my explanation makes sense.
Thanks in advance - LB