if i run two sets of 300 kcmil copper for the 600A 3ph, would that comply? Or do i need to reduce ampacity because of more then three conductors in the raceway?
 
amazing electric said:
if i run two sets of 300 kcmil copper for the 600A 3ph, would that comply?

It could, depending on the calculated load.

Or do i need to reduce ampacity because of more then three conductors in the raceway?

Yes, 80%

Two sets of 90C 300 CU in a single raceway will have a capacity of only 512 amps.

240.4(B) will allow this to be used with a 600 amp breaker, but the calculated load is limited to less then 512 amps.

90C 300 CU has a ampacity of 320 amps.

320 * 2 *.8 = 512
 
Last edited:
amazing electric said:
if i run two sets of 300 kcmil copper for the 600A 3ph, would that comply? Or do i need to reduce ampacity because of more then three conductors in the raceway?


I'm unsure if any configuration using copper conductors would be the cheapest installation method.

What is the most economical way to feed 600A 3PH service?
 