Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
When running a feed for say a 20, 30 or 40a motor such as an exhaust fan etc. is a separate ground required or can you use the conduit as a ground. I am thinking it would not just be hot or hots(depending on poles/phases) and neutral? THanks.

What are the parameters for wiring motors and a separate gorund? Thanks.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
When running a feed for say a 20, 30 or 40a motor such as an exhaust fan etc. is a separate ground required or can you use the conduit as a ground. I am thinking it would not just be hot or hots(depending on poles/phases) and neutral? THanks.

What are the parameters for wiring motors and a separate gorund? Thanks.

You can use metal raceway as an EGC but depending on the flexible connection from the disconnect to the motor you may need an internal EGC.

Look at art. 250.118
 