A A-1Sparky Senior Member Location Vermont Aug 16, 2012 #1 Is there any issue code-wise with having the load wires on the top lugs and the line wires on the bottom lugs of a feed- through breaker? I've got a conductor length problem.
Is there any issue code-wise with having the load wires on the top lugs and the line wires on the bottom lugs of a feed- through breaker? I've got a conductor length problem.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 16, 2012 #2 None unless the breaker is marked "Line" and as long as you don't violate 404.7
A A-1Sparky Senior Member Location Vermont Aug 16, 2012 #3 No "line" or "load" labeling. I'll have to look up 404.7. Thanks Augie.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 16, 2012 #4 A-1Sparky said: No "line" or "load" labeling. I'll have to look up 404.7. Thanks Augie. Click to expand... In a nut shell, "ON" can't be handle down.
A-1Sparky said: No "line" or "load" labeling. I'll have to look up 404.7. Thanks Augie. Click to expand... In a nut shell, "ON" can't be handle down.