Feed-Through Breaker

Status
Not open for further replies.

A-1Sparky

Senior Member
Location
Vermont
Is there any issue code-wise with having the load wires on the top lugs and the line wires on the bottom lugs of a feed- through breaker? I've got a conductor length problem.:cool:
 
None unless the breaker is marked "Line" and as long as you don't violate 404.7
 