rszimm
Member
- Location
- Tucson, AZ
I have a 125A subpanel fed with a 125A breaker in the main panel (200' away). I have a 100A fused disconnect (with 100A fuses) directly adjacent (less than 10') to the sub-panel fed with feed-through lugs. The load side of the disconnect feeds a secondary 100A sub-panel.
So, I believe the tap rule (240.21(B)(1)) applies. So the question is twofold:
So, I believe the tap rule (240.21(B)(1)) applies. So the question is twofold:
- Can I use a 100A disconnect here. (99.9% sure the answer is yes)
- Do the conductors between the sub-feed lugs and the disconnect need to be sized at 100A or 125A? (again, about 90% sure the tap rule allows me to use 100A sizing, but I just wanted to be sure)