I am not an electrician by trade, but rather an researcher/course developer on PV electrical systems. Often times, I see things that are code compliant and have to explain or are asked questions as to why they are compliant. Such as:
Per 240.21, overcurrent protection devices must be placed at the point where the feeder conductors receive their power.
A common practice is to have feeders from "feed through panels" supply sub panels that have a MOCPD. Given 240.21, why is an ocpd not required at those feed through lugs from the main panel? The general statement that I hear is that the feeder is an extension of the bus, but I am looking for the article or explanation that allows this practice to be code compliant.
Per 240.21, overcurrent protection devices must be placed at the point where the feeder conductors receive their power.
A common practice is to have feeders from "feed through panels" supply sub panels that have a MOCPD. Given 240.21, why is an ocpd not required at those feed through lugs from the main panel? The general statement that I hear is that the feeder is an extension of the bus, but I am looking for the article or explanation that allows this practice to be code compliant.