Feed Through Panel

Status
Not open for further replies.

jamesguy10

Senior Member
Location
Amsterdam NY
If i have a 200 amp main breaker panel, with feed through lugs at the bottom feeding another panel, can a SE feed the second panel with seperate #2 grounds run from both panels to the ground rods? The feed through lugs are protected by the main breaker, so there is no grouping disconnect problems.
 
jamesguy10 said:
If i have a 200 amp main breaker panel, with feed through lugs at the bottom feeding another panel, can a SE feed the second panel with seperate #2 grounds run from both panels to the ground rods? The feed through lugs are protected by the main breaker, so there is no grouping disconnect problems.

No. The EGC must be routed with the ungrounded and neutral conductors. 250.134(B)
 
James, kudos for trying to find a NEC compliant way, instead of just doing it, but the fact remains - you need to replace that SEU with SER, no matter the difficulty.
 
JohnJ0906 said:
James, kudos for trying to find a NEC compliant way, instead of just doing it, but the fact remains - you need to replace that SEU with SER, no matter the difficulty.

Nicely put and I agree. :smile:
 
I kinda thought i would have to refeed the old panel....... They do it like i said all the time around here on modulars, not that it makes it right...
 
jamesguy10 said:
I kinda thought i would have to refeed the old panel....... They do it like i said all the time around here on modulars, not that it makes it right...
ooooh... Seperate structures? That was probably okay up until the 2008 NEC.
 