Feed through panel

Status
Not open for further replies.

newt

Senior Member
Can you feed the busbar on a feed through panel instead of the breaker, as long as there is not more then six spaces for breakers? This is a main service panel. For example section 230.90A exception 3.
 

haskindm

Senior Member
Location
Maryland
Re: Feed through panel

As long as the panel is listed as suitable for use as service equipment, this should be OK. I once used a 4-circuit panel in a situation such as this. My thinking was, 4 circuits is less than 6, so it should be OK. The inspector pointed out to me that the listing said that it was "suitable for use as service equipment only when protected by not more than 2 overcurrent devices".
 

jwelectric

Senior Member
Location
North Carolina
Re: Feed through panel

Also read 408.34 and 408.36.
If 10% or more of the over current devices be 30 amps or less and use the grounded (neutral) this panel will require a main
:)
 