Feed thru for GFCI

Status
Not open for further replies.

teejer

Member
Is it permissible under the NEC to use the feed thru provision on GFCI recptacles to feed other devices(lights, etc) besides receptacles. I realize that no GFCI protection would be provided or needed for the non-receptacle devices, but it is merely for wiring convenience sake. We are begining to make UL listed outdoor electrical equipment that contains a feed thru GFCI receptacle on a 20 amp circuit and I want to be able to offer that feed thru option to end users if it is allowed. Thanks for your time.
 
teejer said:
I realize that no GFCI protection would be provided or needed for the non-receptacle devices
A branch circuit downstream of the Load terminals of a GFCI receptacle is indistinguishable from the branch circuit that is downstream of a GFCI breaker in a panelboard.

One example of "required" GFCI protection of a non-receptacle load is an exhaust fan mounted over a residential shower or bathtub. The requirement is not in the NEC, rather it comes from the manufacturer's instructions and/or the UL requirements in the White Book.
 