Im working on a shell warehouse building where a lot of the equipment may end up being 208v in certain areas so the transformer may end up handling the entire load. The incoming voltage is 480/3.
For a 150 kVA transformer, would it be permissible to feed a 480v panel from the MDP, then use feed thru lugs to feed the transformer right from the lugs within the panel provided the conductors were the same size from the MDP, thru the panel, to the transformer primary? Or, would I need to use a 200A sub-feed breaker within the 200A panel?
Normally I would provided primary protection for the xfrmr within the 480v panel but because the entire load may be 208v, im having an issue with this.
Thanks
For a 150 kVA transformer, would it be permissible to feed a 480v panel from the MDP, then use feed thru lugs to feed the transformer right from the lugs within the panel provided the conductors were the same size from the MDP, thru the panel, to the transformer primary? Or, would I need to use a 200A sub-feed breaker within the 200A panel?