Davebones

Senior Member
Can I come off a transformer to 400 amp main breaker in a feed thru panel, then come off the feed thru lugs to a wireway and tap off of wireway to 2 200amp fusible disconnects?The feed to wireway will be rated 400amps while the taps to each fusible disconnect will berated 200amps.
 
Davebones said:
Can I come off a transformer to 400 amp main breaker in a feed thru panel, then come off the feed thru lugs to a wireway and tap off of wireway to 2 200amp fusible disconnects?The feed to wireway will be rated 400amps while the taps to each fusible disconnect will berated 200amps.

Depends on the distance involved from the 400A main to the 200A disconnects....plus a few other tap rules.
As George said....read 240.21(B).

steve
 
Davebones said:
Not more than 10' in long .
Unless it is not more than 25' long.

Yes, 240.24(B) will allow this type of installation. The 10' maximum length is for when the tap cables are less than 1/3 the feeder device (in this case 400A/3 = 134A).
 