GlennG

Member
Location
Hicksville, NY
I just looked at a detached single car garage. I am debating a small 4 circuit sub panel vs just pulling 2, 20 amp circuits out. If someone could help me with some code references, i remember reading that you are limited to pulling I think 2 circuits out, but I'm not sure. If someone could give me some info on where i can read up that would be great. Thanks
 
You are not limited to two circuits.
A MWBC (multi wire branch circuit) is considered a single circuit.
 
I always prefer the sub panel but look at art.225.30 and all of Part II.. Also look at 250.32 for the grounding electrode and the egc
 
You are not limited to two circuits.
A MWBC (multi wire branch circuit) is considered a single circuit.

If you need more than one MWBC then you have to install a sub panel with a feeder. Also if your subpanel has more than 6 disconnects you need to have a main disconnect.
 
Ask the client what they are going to do in the garage (worst case) , address the service.

I prefer the application of a sub-panel, myself! :) Climate, activity, IE the actual usage are all in play.
 
The customer will just be using the garage to park a car, and it is just big enough for that. There will be no type of work shop or anything like that, just a opener and a few lights. My original thought was a sub panel until i saw the scale of the job and found out what they want to have in it. A sub panel would definitely be a nicer job IMO but i feel it is slightly unnecessary. The contractor is concerned cost so I wanted to way the options. thanks for the responses.
 
Running 2 20A circuits out there will save you on the subpanel and driving 2 ground rods. If the garage is just big enough to fit a car and nothing else and the customer doesn't have any specific plans, then 2 20A circuits may be plenty.

I usually run into a double pole switch as a disconnect and then run one circuit to the receptacles and the other circuit to the lights and door opener.
 
Running 2 20A circuits out there will save you on the subpanel and driving 2 ground rods. If the garage is just big enough to fit a car and nothing else and the customer doesn't have any specific plans, then 2 20A circuits may be plenty.

I usually run into a double pole switch as a disconnect and then run one circuit to the receptacles and the other circuit to the lights and door opener.

When you say 2 -20 amp circuits I think you mean one MWBC. Yes?
 
Running 2 20A circuits out there will save you on the subpanel and driving 2 ground rods. If the garage is just big enough to fit a car and nothing else and the customer doesn't have any specific plans, then 2 20A circuits may be plenty.

I usually run into a double pole switch as a disconnect and then run one circuit to the receptacles and the other circuit to the lights and door opener.

I agree given the paramters mentioned. 2-20 amp circuits on a MWBC with a 2 pole snap switch disconnect should be adequate.
 
"2 -20 amp circuits".......you should install one 15 amp MWBC since you should not be using a 20 amp circuit for the lights, heck even one dedicated garage 15 amp circuit would work for a bare bones single car garage
 
"2 -20 amp circuits".......you should install one 15 amp MWBC since you should not be using a 20 amp circuit for the lights, heck even one dedicated garage 15 amp circuit would work for a bare bones single car garage

Why shouldn't he use 20a for the lights?
 
Only other thing to think about is if an electric car is ever in their future. If so, you'd want a 40 to 50 amp feeder to the garage. You could pull 8-3 now and just use it as an oversized 15 or 20 amp MWBC. Then, if they want a car charger, they can replace the disconnect with a panel. So do they want to pay for just the minimum, upsized wire only, or go with a full up feeder and panel.
 
I would at least upsell them on a 1" PVC conduit even if you only pull 2 20's out there. That way they can pull larger out there down the road. The minimal cost of the conduit VS re digging a ditch later down the road is a plus. I also try to sell three ways for the lighting so they can be controlled from the house too.
 