Hello,
Just want to check my wire size. I am feeding a 3Ph 30KVA 480 IN 240 OUT transformer from a 480 buss-way about a 20' run. would i be able to use #4 AWG THHN wire to feed the transformer? the transformer will be running a heat tunnel that's rated at 64amp 240V 3Ph the tunnel has a cord with #2 AWG wire.
Thanks,
Steve
Just want to check my wire size. I am feeding a 3Ph 30KVA 480 IN 240 OUT transformer from a 480 buss-way about a 20' run. would i be able to use #4 AWG THHN wire to feed the transformer? the transformer will be running a heat tunnel that's rated at 64amp 240V 3Ph the tunnel has a cord with #2 AWG wire.