Feedback Transformer for SPRS neutral float in open circuit test w.r.t ground

Status
Not open for further replies.

anisincool

New User
Location
india
Feedback transformer used for slip power recovery system. In this Hv side 6.6KV and LV have two winding delta and Wye both output Phase to phase 413V. my question is when we supply 6.6KV and secondary make open. In this situation we found that line voltage is R-Y= 390, Y-B 393, B-R 393V. but phase to ground found R-E= 225V, B-E = 190, Y-E = 300 and neutral point of Wye ungrounded. While both LV open how?
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
I may not be able to help. I don't know what a "slip power recovery system" is. Nor do I know what a part a "Feedback transformer" plays. A one-line would help.

Although it coud be as simple as:

For un-grounded transformer outputs, the line-to-ground voltage is undefined. It can be about anything

ice
 