To provide an accurate answer we would need to know what the calculated load is and if there is a single 1200A service disconnect or multiple.I have a set of plans that calls out for (3) parallel 500 mcm copper feeders for a 1200A main service. The 75 degree column says 380A for 500. So that would be 1140A. Is this the correct size wire for the feeders?
Sent from my iPhone using Tapatalk
So the conductors you are talking about, are they the service conductors or feeders?This is a main service. From the utility transformer
Sent from my iPhone using Tapatalk
I concur. OP please don't use the term "service feeder" or refer to service conductors as feeders, it is very confusing.Since the single OCPD is 1200 amps you need 1200 amps or more worth of conductors. No way around that.
No you cannot. It was very very common in the past to call this setup "close enough", or use the next size up rule above 800 amps, or whatever the thinking was, who knows.....This is a secondary service conductor from a utility company transformer for an industrial facility. The service Main is a single 1200A. What’s there currently is (3) sets of 500 mcm.
So the existing 1200A service has (3) sets of 500 mcm. This is also what is called out to be replaced with new, except a neutral is being added to the service.
Everything is being replaced as is currently exact the neutral is being added.
My original question was can we install (3) sets of 500 mcm on this 1200A main? I didn’t know if there was some exceptions or other calculations that would allow this?
Sent from my iPhone using Tapatalk
Probably was, OP said existing was "Delta"I sort of wonder why there was no neutral in the original install unless it was originally a corner grounded or ungrounded delta service.