feeder bond bushing

Status
Not open for further replies.

hdt1980

Member
Location
Fairfax, VA
More information is need to help. Are you pulling in EMT? PVC?

If EMT or any other metallic tubing, then yes you are required to have ground bushings, make sure it is continuous as well.

-HDT
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For the most part bonding bushings are not required very often. If you're over 250 volts and have concentric or eccentric KO's that would be different.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The fact that you are installing an internal EGC of the wire type does not change any of the installation rules for a metallic raceway.
 

kwired

Electron manager
Location
NE Nebraska
More information is need to help. Are you pulling in EMT? PVC?

If EMT or any other metallic tubing, then yes you are required to have ground bushings, make sure it is continuous as well.

-HDT
Based on NEC only this is not true. Over 250 volts or when encountering concentric/eccentric knockouts often requires additional bonding methods and some equipment is listed to not require additional bonding in those instances. Service raceways are the other case where additional bonding methods may be required.
 