Going over practice questions to prepare for master electrician exam and I have a question,
An individual apartment in a multi-family dwelling is supplied by 255-amp THW copper feeders. The feeder conductors are protected by 225-amp breakers from the main 800 amp building service. The water piping systems in the apartment is metal but, tap is pvc. What size equipment bonding jumper is needed?
Shouldn't the answer be #2 copper?
How I came with this, I went to table 310.16 and figured feeder conductor is 250AWG.
Then I went to table 250.102(C)(1) and got #2 from the table.
Answer shows it should be #4.
HELP!
An individual apartment in a multi-family dwelling is supplied by 255-amp THW copper feeders. The feeder conductors are protected by 225-amp breakers from the main 800 amp building service. The water piping systems in the apartment is metal but, tap is pvc. What size equipment bonding jumper is needed?