Please see the following problem I'm having with a local inspector.
We have 5-225a and 1-100a rated MLO sub-panels on our project all fed from an MDP.
2-fed with 225 amp OCP and 225 amp feeders
1-fed with 150 amp OCP and 150 amp feeders
2-fed with 110 amp OPC and 110 amp feeders
1-100a panel fed with 70 amp OCP and 70 amp feeder
The inspector is refusing to sign off and issue our permit saying this is a code violation.
He states that all OCP devices and feeders must match the name plate rating of the MLO sub-panels.
Ie:5-breakers and feeders sized at 225 amps
and 1-breaker and feeder at 100 amps.
I feel he is wrong but he is standing his ground.