Hello All! This is my first post so please go easy on me. Long time reader of the forums however.
I have a wireway with several taps into fused disconnects feeding 2 chillers and 3 pump motors. It is currently fed from a 208V 3 phase 600A circuit breaker. We are replacing the chillers with slightly larger ones and I need to see if the 600A breaker is large enough or if we need to go to a larger size. Here is my thought process.
I am using the 2017 NEC and going through what it says in 440.110 (C).
Full-Load Current Calculation
Chiller 1 Compressor A - RLA = 48A
Chiller 1 Compressor B - RLA = 48A
Chiller 1 Compressor C - RLA = 122A
Chiller 2 Compressor A - RLA = 48A
Chiller 2 Compressor B - RLA = 48A
Chiller 2 Compressor C - RLA = 122A
Pump 1 - 3 HP (10.6A from 430.250)
Pump 2 - 3 HP (10.6A from 430.250)
Pump 3 - 3 HP (10.6A from 430.250)
Total full load current = 467.8A
Total Full load current * 115% = 537.97A
Locked Rotor Current Calculation
Chiller 1 Compressor A - LRA = 351A
Chiller 1 Compressor B - LRA = 351A
Chiller 1 Compressor C - LRA = 1010A
Chiller 2 Compressor A - LRA = 351A
Chiller 2 Compressor B - LRA = 351A
Chiller 2 Compressor C - LRA = 1010A
Pump 1 - 3 HP (71A from 430.251(B))
Pump 2 - 3 HP (71A from 430.251(B))
Pump 3 - 3 HP (71A from 430.251(B))
Total Locked Rotor Current = 3637A
Now here is where I am having a problem. When I go to look at Table 430.251(B) for the equivalent HP based on the total LRA I see that the table stops at 3207A. which isn't very close to the 3637A that I have calculated. The 3207 LRA is the equivalent of a 200HP motor according to the table. a 200HP motor has 528 FLA according to 430.250.
Does this mean that for any LRA over 3207A we just use a 200HP motor for the rest of the calculation?
Lets say for arguments sake that my total LRA was MUCH higher than 3207A. What do we do then?
Thanks All!
I have a wireway with several taps into fused disconnects feeding 2 chillers and 3 pump motors. It is currently fed from a 208V 3 phase 600A circuit breaker. We are replacing the chillers with slightly larger ones and I need to see if the 600A breaker is large enough or if we need to go to a larger size. Here is my thought process.
I am using the 2017 NEC and going through what it says in 440.110 (C).
Full-Load Current Calculation
Chiller 1 Compressor A - RLA = 48A
Chiller 1 Compressor B - RLA = 48A
Chiller 1 Compressor C - RLA = 122A
Chiller 2 Compressor A - RLA = 48A
Chiller 2 Compressor B - RLA = 48A
Chiller 2 Compressor C - RLA = 122A
Pump 1 - 3 HP (10.6A from 430.250)
Pump 2 - 3 HP (10.6A from 430.250)
Pump 3 - 3 HP (10.6A from 430.250)
Total full load current = 467.8A
Total Full load current * 115% = 537.97A
Locked Rotor Current Calculation
Chiller 1 Compressor A - LRA = 351A
Chiller 1 Compressor B - LRA = 351A
Chiller 1 Compressor C - LRA = 1010A
Chiller 2 Compressor A - LRA = 351A
Chiller 2 Compressor B - LRA = 351A
Chiller 2 Compressor C - LRA = 1010A
Pump 1 - 3 HP (71A from 430.251(B))
Pump 2 - 3 HP (71A from 430.251(B))
Pump 3 - 3 HP (71A from 430.251(B))
Total Locked Rotor Current = 3637A
Now here is where I am having a problem. When I go to look at Table 430.251(B) for the equivalent HP based on the total LRA I see that the table stops at 3207A. which isn't very close to the 3637A that I have calculated. The 3207 LRA is the equivalent of a 200HP motor according to the table. a 200HP motor has 528 FLA according to 430.250.
Does this mean that for any LRA over 3207A we just use a 200HP motor for the rest of the calculation?
Lets say for arguments sake that my total LRA was MUCH higher than 3207A. What do we do then?
Thanks All!